Bay Area Municipal Transmission group (BAMx)
Submitted 03/14/2022, 02:39 pm
Submitted on behalf of
Silicon Valley Power and City of Palo Alto Utilities
1.
Comment on chapter 1 Introduction:
The Bay Area Municipal Transmission group (BAMx)[1] appreciates the opportunity to comment on the California Independent System Operator (CAISO) Draft 2022-2023 Transmission Planning Process (TPP) Unified Planning Assumption and Study Plan (Study Plan). The comments and questions below address the Study Plan posted on February 18, 2022, and discussed during the February 28, 2022 stakeholder meeting. We applaud the CAISO’s desire to work with Stakeholders to enhance each year’s plan. We look forward to working with the CAISO on this collaborative process.
[1] BAMx consists of City of Palo Alto Utilities and City of Santa Clara, Silicon Valley Power.
2.
Comment on chapter 2 Reliability Assessment:
BAMx Supports the CAISO’s Plan to Not Model the “On Hold” Projects
There are some transmission projects “on hold,” such as Moraga-Sobrante 115 kV Line Reconductor, North of Mesa Upgrade (formerly Midway-Andrew 230 kV Project), and Wheeler Ridge Junction Substation.[1] The Study Plan states that these projects put on hold will not be modeled in the starting base case. BAMx supports this process. While much work has been done to evaluate previously approved projects as a one-time effort, part of the next year’s Study Plan should include a formal process to continually monitor such previously approved projects. BAMx’s participation in the PG&E Stakeholder Transmission Asset Review (STAR) process has illustrated for us how PG&E evaluates which projects receive priority for funding and the many reasons projects can be delayed. Participating in that process makes BAMx even more convinced that the CAISO should reaffirm the continued need for previously approved projects, especially those that are not yet under construction.
[1] CAISO Draft 2021-2022 Transmission Plan, January 31, 2022, pp.374-376.
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
Proposed Policy-Driven Scenario Assessment Appears to Be Very Limited
The Study Plan indicates that in the 2022-2023 transmission planning cycle, the CAISO will undertake a special study to evaluate the potential reliability impacts to the transmission facilities based on a high electrification scenario.[1] CAISO’s February 28th presentation at the stakeholder meeting indicates that this “sensitivity” portfolio will be a special study, which appears to give the impression that it will not be used for the policy-driven assessment in the current planning cycle. However, a follow-up discussion with the CAISO during the February 28th stakeholder meeting led BAMx to believe that the “High Electrification” sensitivity scenario will be indeed used for the policy-driven assessment. BAMx urges that the Final Transmission Study Plan clearly state how the “High Electrification” sensitivity scenario will be used for the policy-driven assessment.
Even if the CAISO chooses to use the “High Electrification” sensitivity scenario, the policy-driven assessment in the current planning cycle seems to be very limited. Per the CAISO’s FERC-approved tariff, a Category 1 policy-driven transmission solution has to be identified to be needed “in the baseline scenario and at least a significant percentage of the stress scenarios.”[2] Historically, the CAISO has studied at least two sensitivity portfolios in its policy-driven assessment. How does the CAISO plan to identify a Category 1 policy-driven transmission project with a base portfolio and a single sensitivity portfolio? BAMx urges the CAISO to clearly lay out its Final Study Plan proposal on this issue. In the absence of multiple sensitivity portfolios, BAMx suggests that any policy-driven transmission project identified in the current transmission planning cycle be designated as only a Category 2 transmission project consistent with the CAISO tariff and the transmission planning Business Practice Manual (BPM).
Locational Guidance, Effectiveness, and Duration of Battery Storage Resources
BAMx has been promoting the remapping of battery storage to very congested areas with high renewable curtailment - as this can help to reduce congestion and curtailment of renewable resources.[3] BAMx agrees with the CAISO that the role of battery storage is expected to continue to grow as a complement to renewable generation and also as a key source of capacity meeting both system capacity needs and local needs.[4] Ultimately, storage resources will be available to meet energy needs during most periods when renewable resources are not available to generate. BAMx agrees that only the incremental interconnection cost for storage projects should be compared to transmission costs when the batteries are located in locally constrained areas.
BAMx applauds the CAISO staff’s efforts in relying on the implementation of Remedial Action Schemes (RAS) and storage solutions in its Preliminary Policy Assessment. As shown in Table 1 (compiled by BAMx )below, the CAISO has effectively and rightfully utilized the existing/planned RAS dispatching portfolio battery storage in charging mode and includes new battery storage as mitigations wherever applicable to mitigate the contingency overloads.
Table 1: Recommended Non-Wires Mitigations*
*Source: November 18th Presentation, “2021-2022 TPP Policy-driven Assessment,” pp. 30-55.
As included in the CAISO’s February 28th presentation[5],
“To the extent that storage resources are required for mitigation of transmission issues identified in the CAISO’s 2021-2022 Transmission Plan, CPUC staff would expect to coordinate with CAISO to enable small adjustments in the CPUC’s mapping of storage resources to allow for the inclusion of these storage resources in the CAISO’s analysis of the 2022-2023 TPP portfolios.”
BAMx supports the CAISO’s plans to transfer such valuable feedback to the California Public Utilities Commission (CPUC) and California Energy Commission (CEC) so that it is incorporated as part of the battery storage mapping exercise in the 2022-2023 TPP cycle. BAMx requests that the CAISO share its suggested incremental changes to the CPUC’s mapping of storage resources with stakeholders as part of the Final Transmission Study Plan.
The resource to Busbar Mapping and Transmission Limit Calculations Need to Take Into Account Prior Project Approvals
As the Study Plan indicates, “(T)he transmission projects that the CAISO has approved will be modeled in the study. This includes existing transmission projects that have been in service and future transmission projects that have received CAISO approval in the 2021-2022 or earlier CAISO transmission plans.”[6] BAMx recognizes the timing issues concerning the Study Plan being developed before the CAISO Board approval of the 2021-2022 TPP. But if the CAISO Board approves certain projects in the 2021-2022 TPP, they will probably have a major effect on the transmission limit calculations and the selection of resources and their mapping. BAMx questions whether the “final” resource to busbar mapping provided by the CPUC for the base portfolio for the 2022-2023 TPP is accurate if certain projects get approval in the 2021-2022 TPP. For example, the Los Banos 500/230kV Transformer Bank constraint is addressed by an Area Delivery Network Upgrade (ADNU), i.e., the Manning 500/230kV substation project that is expected to increase the expected on-peak full capacity deliverability (FCDS) capability in the Westlands zone by 446MW.[7] See the screenshot included in Figure 1 below. Furthermore, the Manning substation may potentially eliminate the Wilson-Storey-Borden 230 kV constraint within Westlands.[8] However, the final mapping does not seem to map the resources recognizing this additional available FCDS capacity. If the CAISO Board approves the new Manning 500/230 kV substation and other transmission projects recommended for approval in the Draft 2021-2022 Transmission Plan, the CAISO needs to update the transmission limit calculations and the resource to busbar mapping accordingly.
Figure 1: Transmission Capability Estimates For Use In The CPUC’s IRP Process
BAMx’s review of the transmission capability document provided to the CPUC for the resource to busbar mapping finds that the costs for transmission upgrades are likely underestimated. For instance, in the Busbar Mapping of the Policy and Reliability Base Case Portfolio, the Manning 500/230 kV substation upgrade is estimated at $370 million as shown in Figure 1 above.[9] However, the Draft 2021-2022 Transmission Plan estimates that the high-cost range for this project would be as high as $485 million. Given the history of cost overruns of the major transmission projects after CAISO approval, BAMx recommends that transmission capability calculations - used for busbar mapping and resource selection in the CPUC’s RESOLVE model - should consistently use the higher range of the capital cost estimates.
Generation Retirements
In the past few TPP cycles, the CAISO has been assuming an arbitrary amount of retirements of generating resources aged 40 years or more.[10] In the Study Plan, the CAISO has indicated that it will not assume retirement based on a resource aged 40 years or more in order to align with the latest CPUC portfolio information. BAMx supports this decision. However, the CPUC Thermal Age Based Retirements Assumptions document includes a list of thermal projects that are assumed to be retired at the age of 40 years.[11] We request the CAISO to provide a clarification on this apparent discrepancy.
Since the continued availability of generation resources is a critical assumption now and likely will get even more critical as time goes by, BAMx suggests a separate stakeholder process covering this topic needs to occur soon. CPUC input in this process will be vital. Alternatives to the retirement of aged generation resources should be generically investigated as part of this process. Since age is only one indicator of the continued viability of a generator, BAMx opposes arbitrarily capping the thermal generators at 40 years in the current planning cycle.
[1] Study Plan, p. 64.
[2] CAISO Fifth Replacement FERC Electric Tariff, Effective as of January 1, 2022, 24.4.6.6 Policy-Driven Transmission Solutions. Also, see the section 4.6.2. Category 1 and Category 2 Policy-Driven Solutions in the CAISO BPM for the Transmission Planning Process.
[3] BAMx Comments on the CAISO 2021-2022 Transmission Study Plan, March 11, 2021.
[4] Draft 2021-2022 Transmission Plan, January 31, 2022, p.31.
[5] Policy-driven Assessment Unified Planning Assumptions & Study Plan, slide #13.
[6] Study Plan, p. 13.
[7] See CPUC portfolio documentation for the 2022-2023 TPP. In particular, “Final busbar mapping results and transmission limit calculation for the base portfolio,” ftp://ftp.cpuc.ca.gov/energy/modeling/BusbarMapping_Dashboard_38MMT_V2022_02_08.xlsx (2_CAISO_Tx_Constraints tab)
[8] Ibid, and CAISO Draft 2021-2022 Transmission Plan, January 31, 2022, p.198.
[9] Ibid.
[10] Study Plan, p.25.
[11] See CPUC portfolio documentation for the 2022-2023 TPP. In particular, “Thermal Age Based Retirements Assumptions.” ftp://ftp.cpuc.ca.gov/energy/modeling/Thermal%20Age%20Based%20Retirements%20Assumptions_V2021_10_15.xlsx
4.
Comment on chapter 4 Economic Planning Study:
The Study Plan states that the economic planning study will quantify the economic benefits for the CAISO ratepayers based on Transmission Economic Assessment Methodology (TEAM).[1] Although the Study Plan does not make it clear, it appears that the TEAM analysis will be applied only to the Base portfolio. An analysis based upon a single baseline scenario is inconsistent with CAISO’s TEAM principles to account for risk and uncertainty.[2] BAMx requests that the Study Plan clearly lays out the broad scope of the Production Cost Modeling (PCM) entailing multiple scenarios as envisioned under TEAM that would be conducted in the determination of the economic-driven transmission projects in the current planning cycle. These scenarios should capture varying levels of load growth, gas prices, hydrological conditions, and different resource plans including varying levels of fossil-fired retirements as envisioned under TEAM.[3]
[1] Study Plan, p.55.
[2] The CAISO TEAM 2017, available at
https://www.caiso.com/Documents/TransmissionEconomicAssessmentMethodology-Nov2_2017.pdf
[3] Ibid. p.3.
5.
Comment on chapter 5 Interregional Transmission Coordination:
One of BAMx’s primary takeaways from the western planning regions’ stakeholder meeting on March 4, 2022 is that the neighboring planning regions of WestConnect and NorthernGrid have not found any regional need for Interregional Transmission Projects (ITPs) thus far. NorthernGrid acknowledged in their March 4th presentation that some ITPs that they evaluated might have some benefits; however, those ITPs were not selected in NorthernGrid’s 2020-21 Regional Plan.[1] Similarly, WestConnect did not identify any regional transmission needs in the 2020-21 regional planning cycle, and as such, did not evaluate any ITPs in 2020-21.[2] As the CAISO evaluates the need for ITPs under the current planning cycle (Year 1 of 2), it is important to recognize that just because the neighboring planning regions have not evaluated the ITPs that are seeking cost allocation from them, it does not mean that these planning regions do not benefit from those ITPs. Therefore, consistent with FERC Order 1000 cost allocation principles, the CAISO’s economic assessment of the ITPs needs to be cognizant of potentially allocating some of the cost of the ITPs to the neighboring planning regions that may benefit from them should the CAISO find any of the ITPs economically viable.
The CAISO needs to comply with Order 1000, and we encourage the adopting of our above recommendations. However, it is clear that even though the FERC Order 1000 process has been in place for the last decade or so, not a single ITP has been approved (or built) by two or more planning authorities. So far, there is not a single example of two or more planning regions agreeing to share costs on a transmission project. That said, some ITP projects are proceeding to construction based upon a subscription model. The CAISO 20-year Transmission Outlook recognizes that the Sunzia and the TransWest Express[3] (TWE) projects are proceeding on that basis. BAMx believes that this is a positive development and that a subscriber model might be the best model to get transmission projects accessing out-of-State (OOS) wind built. BAMx believes such a mechanism ensures Load Serving Entities (LSEs) choose to buy power from the most cost-effective projects. Besides reducing the impact on the Transmission Access Charge (TAC), it promotes cost causation and benefits-based recovery mechanisms for those projects needed to deliver OOS wind generation. BAMx believes that the subscriber model could apply to the remaining OOS projects, such as SWIP-North and Cross-Tie.
[1] NorthernGrid 2022 Annual Western Interregional Coordination, March 4, 2022, pp.5-6.
[2] WestConnect 2022 Annual Western Interregional Coordination, March 4, 2022, p.55.
[3] Through the Open Solicitation, TransWest sought interest in the TWE Project from potential customers. See https://transwestexpress-os.com.
6.
Comment on chapter 6 Other Studies:
No comments at this time.
7.
Please provide any additional comments:
Need for CAISO to Provide a Timely Response to Stakeholder Comments
Historically, the CAISO has been generally responsive to the stakeholder comments. For example, it typically posts its responses to the stakeholder comments on reliability assessment (October) sometime in mid-November. However, that was not the case in the 2021-2022 TPP cycle. As of March 1, 2022, the CAISO has not posted its responses to stockholders’ comments dated October 10, 2021 and December 6, 2021. It is incredibly challenging to respond and comment on specific aspects of the Draft Plan without knowing the CAISO’s responses to prior concerns raised by BAMx and other stakeholders. Therefore, BAMx requests that the Final Study Plan expand the schedule for the 2022-2023 planning cycle to include the expected timing for the CAISO responses to the stakeholder comments.[1]
Need for a Separate Stakeholder Process to Consider Dynamic Transmission Line Ratings
Transmission line ratings represent the maximum transfer capability of each transmission line. Appropiate ratings are dependent on weather conditions.[2] One such example is PG&E’s recommendation that the CAISO evaluate the implementation of dynamic ratings on the Midway–Whirlwind 500 kV line.[3]
On February 17, 2022, Federal Energy Regulatory Commission (FERC) launched an inquiry to examine whether the use of dynamic line ratings (DLRs), which are based on a wide range of weather and line-specific factors affecting the operation of electric transmission lines, would help ensure just and reasonable wholesale rates by improving the accuracy and transparency of line ratings.[4] BAMx requests CAISO to start a stakeholder process in parallel to the 2022-2023 TPP cycle, to evaluate the relative benefits, costs, and challenges of dynamic line rating implementation.
The CAISO’s transmission planning analysis utilizes the summer emergency ratings that were developed assuming weather conditions deemed appropriate for the traditional summer net peak hour (likely HE16 for most regions). However, it has become standard practice to study the net peak and also the load peak. It appears that by using the temperature assumptions for the load peak hour, the CAISO is underestimating transmission line capacity for the net peak studies and, in turn, the local area import capabilities. In the proposed stakeholder process, the CAISO’s Participating Transmission Owners (PTOs) can present their opinion on the role of dynamic line ratings going forward. Although we would expect some circumstances might lead to different rating methodologies among PTOs, it would be very informative to have a single stakeholder process to allow comments on the proposed methods.
BAMx Appreciates The Opportunity to Comment
BAMx appreciates the opportunity to comment on the draft Study Plan. BAMx would also like to acknowledge the significant effort of the CAISO staff in developing the Study Plan to date, as well as the CAISO staff’s willingness to work with the stakeholders in the process of developing the Study Plan. We hope to work with the CAISO staff to continue to improve and enhance the Study Plan.
[1] Study Plan, pp.5-6: Table 1.1-1: Schedule for the 2022-2023 planning cycle.
[2] Transmission line ratings could be based on factors beyond forecasted ambient air temperatures and the presence of solar heating. Applying these factors to reflect other weather conditions like wind, cloud cover, solar heating intensity and precipitation, as well as transmission line conditions such as tension or sag, could lead to greater accuracy and enable greater power flows.
[3] PG&E’s comments on the on the Draft 2021-2022 Transmission Plan, dated February 22, 2022.
[4] https://www.ferc.gov/news-events/news/ferc-opens-inquiry-use-dynamic-line-ratings-promote-grid-efficiency
California Public Utilities Commission - Public Advocates Office
Submitted 03/14/2022, 05:06 pm
1.
Comment on chapter 1 Introduction:
The Public Advocates Office at the California Public Utilities Commission (Cal Advocates) provides these comments on the 2022-2023 Transmission Planning Process (TPP) Unified Planning Assumptions and Study Plan (2022 Draft Study Plan). Cal Advocates is an independent consumer advocate with a mandate to obtain the lowest possible rates for utility services, consistent with reliable and safe service levels, and the state’s environmental goals.[1]
Recommendations on Transmission Planning Process Project Analysis and Descriptions
As stated in the California Independent System Operator Corporation’s (CAISO) Business Practice Manual (BPM) document for the CAISO TPP, one purpose of the TPP is to identify alternatives to proposed reliability and policy infrastructure solutions.[2] To confirm whether a proposed project is the low-cost, best-fit solution, it is necessary to evaluate and compare the proposed project to feasible alternatives. A policy-driven project can, in part, be justified based on its costs compared to alternatives.[3] Thus, to fully justify a policy-driven project, the CAISO should consider feasible alternatives and their associated costs. Cal Advocates also recommends the CAISO present its alternative analysis in a consistent manner for proposed reliability and policy projects in the 2022-2023 TPP cycle and future TPP cycles. As such, Cal Advocates recommends the following:
- Provide Non-Wire Alternative Analysis
Alternative analysis should consider low-cost grid enhancing technologies, such as energy storage and reactive support devices consistent with the CAISO’s Tariff.[4] The CAISO’s BPM for the TPP requires that the CAISO to consider non-transmission alternatives as mitigation solutions for identified grid needs.[5], [6] Cal Advocates’ comments on the 2021-2022 Draft Transmission Plan (2021 Draft Plan) noted that the CAISO’s alternative analysis was limited to Remedial Action Schemes,[7] and the CAISO did not consider other grid enhancing technologies.[8] Remedial Action Schemes are system tools that do not add system capacity.
The National Association of Regulatory Utility Commissioners (NARUC), in its comments on the Federal Energy Regulatory Commission (FERC) Advanced Notice of Proposed Rulemaking, Building for the Future Through Electric Regional Transmission Planning and Cost Allocation and Generator Interconnection (FERC RM21-17-000), stated support for providing a “clear pathway” for consideration of alternative transmission solutions, “including grid enhancing technologies, non-transmission technologies, and hybrid programs for efficiency, load control, distributed generation and storage in the regional planning process.”[9]
NARUC further stated that,
transmission planning should focus on identifying multiple cost-effective possibilities to solve a need and should consider a portfolio of transmission projects, as well as non-wires alternatives to new transmission, to optimize efficiencies, facilitate interconnections and promote cost containment over a long-term planning horizon.[10]
Cal Advocates agrees with these NARUC comments and requests that CAISO consider the range of feasible grid enhancing technologies, such as Smart Wires, as alternatives to proposed projects.[11]
- Require More Project Information Detail
As specified in our 2021 Draft Plan comments, Cal Advocates recommends the CAISO and utilities provide more detailed information on the alternatives considered by the CAISO, their costs, and the costs for all the proposed project’s major components including any contingency costs.[12]
The Bay Area Municipal Transmission Group also raised similar concerns with the alternative analysis provided in the 2021-2022 TPP cycle stating that:
In some cases, it appears the transmission alternatives have not yet been fully developed, screened, and analyzed. Alternatives are often discussed qualitatively but never quantitatively compared with the proposed alternative. For instance, the stakeholders do not have access to any “change” power flow cases for the policy-driven transmission analysis and documentation underlying the recommended projects’ needs.[13]
Typically, the TPP includes rough estimated project costs or book-end project costs. Cal Advocates recommends that the CAISO include a more substantial and detailed breakdown of the major project components’ costs and contingency costs. Without this essential project information, the CAISO Board and stakeholders cannot confirm whether the proposed projects are justified based on their costs.
To ensure that the 2022-2023 TPP cycle and future TPP cycles sufficiently consider project alternatives and provide adequate project information, Cal Advocates also recommends the following revisions to the CAISO’s BPM document for the TPP.
4.3.3.1. Reliability-Driven Solutions, Merchant Solutions and Solutions Needed to Maintain the Feasibility of Long-Term CRRs Submissions
(c ) Planning Level Cost Data
- Project construction costs estimate with costs provided for each project component including contingencies, schedule, anticipated operations, and other data necessary for the study. Cost data is not necessary for merchant projects.
- Alternative analysis illustrating the alternative’s capacity to address the reliability, economic or policy need and estimated costs for all project components and reasons provided for any anticipated upgrades and associated costs to support the alternative.[14]
- Require Vetting of Project Cost Information
Cal Advocates recommends that the CAISO, or a third party hired by the CAISO, vet incumbent utilities’ project cost information to confirm that the costs for proposed utility projects and project alternatives are reasonable.
- Costs and Ratepayer Impact
To improve the CAISO TPP stakeholder process, Cal Advocates recommends that the CAISO provide the costs and ratepayer impacts for all transmission projects recommended for approval in the 2022-2023 TPP cycle. The CAISO should analyze and formally present ratepayer cost impacts, such as cumulative additions to regional and local transmission revenue requirements and impacts to the transmission access charge (TAC), when discussing proposed projects. Merely providing estimated capital costs does not provide actionable information for meaningful stakeholder engagement on ratepayer impacts.
[1] Cal. Pub. Util. Code § 309.5.
[2] Business Practice Manual for Transmission Planning Process Version 21.0, CAISO, June 30, 2020, (BPM-TPP), p. 13.
[3] BPM-TPP, p. 43.
[4] CAISO Tariff Section 24 Comprehensive Transmission Planning Process, September 9, 2020 (Section 24), 24.4.6.2 Reliability Driven Solutions.
[5] BPM-TPP, pp. 51-52.
[6] Section 24, 24.4.5 Determination of Needed Transmission Solutions.
[7] A remedial action scheme is designed to respond to predetermined system conditions and automatically take corrective actions that may include but are not limited to adjusting or tripping generation, tripping load or isolating a faulted system.
[8] Cal Advocates Comments on the Draft 2021-2022 Transmission Plan, February 24, 2022, pp.4-12.
[9] Motion to Intervene and comments of the National Association of Regulatory Utility Commissioners, Docket No. RM21-17-000, October 12, 2021, p. 9.
[10] Motion to Intervene and comments of the National Association of Regulatory Utility Commissioners, Docket No. RM21-17-000, October 12, 2021, p. 12.
[11] Smart Wires are devices that assist with digitally controlling the grid by allowing grid operators to change the flow of energy on specific lines, if necessary.
[12] Cal Advocates Comments on the Draft 2021-2022 Transmission Plan, February 24, 2022, pp.1-2.
[13] Bay Area Municipal Transmission Group Comments on Draft 2021-022 Transmission Plan, February 22, 2022, p. 2.
[14] BPM-TPP, pp. 35-36.
2.
Comment on chapter 2 Reliability Assessment:
Inverter-Based Resources Reliability Assessment Studies
Cal Advocates recommends that the CAISO provide more detail regarding the small signal stability analysis studies described in Section 2.14 of the 2022 Draft Study Plan.[1] This analysis will contribute to a better understanding of potential control instability of inverter-based resources under the given resource portfolios. The resource portfolios will likely have transient periods dominated by power generation by inverter-based resources such as wind, solar, or energy storage. Greater detail is necessary to fully understand how much frequency response or voltage support can be reliably provided by inverter-based resources without the use of grid-forming inverters (GFMI) or synchronous machines.[2]
The Western Electricity Coordinating Council (WECC),[3] Electric Power Research Institute (EPRI),[4] and National Renewable Energy Lab (NREL)[5] have started studies and processes to identify GFMI requirements and costs. The CAISO should outline explicit study parameters to determine the limitations of current inverter technology as well as the potential cost impacts of GFMI to fulfill future frequency response and voltage support requirements with decreasing system inertia.
Integrated Resource Portfolio Resources Considered
Per CPUC Decision (D.) 22-02-004, the CAISO should factor in the uncertainty associated with the busbar mapping results for out-of-state (OOS) wind as provided in the Modeling Assumptions for the 2022-2023 TPP. Cal Advocates recommends the CAISO compare the proposed selection of 1,062 MW to 1,500 MW of Wyoming wind resources with feasible alternatives to determine the most cost-efficient option. D.22-02-004 acknowledges “uncertainty around the exact amount of [OOS] resources that will ultimately be needed, and also the amount that can be imported through existing transmission.” [6] To account for this uncertainty, the CPUC states, “should additional information from the 2021-2022 TPP prove useful, [CPUC] staff could consider an addendum to the busbar mapping produced with this proposed decision, to take into account identification of preferable specific locations and injection points for the mapping of the 1,500 MW of out of state (OOS) wind resource.”[7]
Evidence was provided during the 2021-2022 TPP that demonstrated that there are potentially lower cost options to access OOS wind. In its comments on the November 18, 2021, stakeholder meeting and on the 2021 Draft Plan, Pattern Energy stated that its SunZia project can deliver “2 to 3 GW of New Mexico wind to the CAISO grid by 2026.” [8] SunZia is a subscriber-based (merchant) project that provides access to New Mexico wind through a combination of existing and new transmission. Merchant transmission projects are projects that do not seek cost recovery through the CAISO transmission access charge (TAC) and are funded by the project sponsor instead.[9]
Cal Advocates recommends that CAISO consider the SunZia project to access the proposed amount of OOS because it is likely a lower cost option to new transmission that is rate-based in CAISO transmission rates. To explain, the SunZia project’s economic viability depends on offering competitive services to load-serving entities (LSEs).[10] This could apply downward pressure on transmission costs. Rate-based projects such as the SWIP-North project, alternatively, would receive a guaranteed rate of return that would be incorporated into the CAISO transmission access charge, which has increased over 255% since 2009.[11]
Cal Advocates also recommends that the CAISO provide an apples-to-apples comparison of all available options (merchant-based versus CAISO rate-based) to access 1,500 MW of out of state wind.
Recommendation: The CAISO’s assessment 1,500 MW of “Wind on New Out-of-State Transmission,”[12] as stated in its 2022 Draft Study Plan, should include an apples-to-apples comparison with all the feasible and likely lower costs options, such as out of state wind from New Mexico.
[1] 2022 CAISO Transmission Draft Study Plan, p. 47.
[2] Lin, Yashen, Joseph H. Eto, Brian B. Johnson, Jack D. Flicker, Robert H. Lasseter, Hugo N. Villegas Pico, Gab-Su Seo, Brian J. Pierre, and Abraham Ellis. 2020. Research Roadmap on Grid-Forming Inverters. Golden, CO: National Renewable Energy Laboratory. NREL/TP-5D00-73476. https://www.nrel.gov/docs/fy21osti/73476.pdf.
[3] Grid-Forming Inverter Based Resources Workshop. Western Electricity Coordinating Council. October 13, 2021.
[4] Grid Forming Inverters: EPRI Tutorial. EPRI, Palo Alto, CA: 2020. 3002018676.
[5] Lin, Yashen, Joseph H. Eto, Brian B. Johnson, Jack D. Flicker, Robert H. Lasseter, Hugo N. Villegas Pico, Gab-Su Seo, Brian J. Pierre, and Abraham Ellis. 2020. Research Roadmap on Grid-Forming Inverters. Golden, CO: National Renewable Energy Laboratory. NREL/TP-5D00-73476. https://www.nrel.gov/docs/fy21osti/73476.pdf.
[6] Decision (D.) 22-02-004, p. 135. Available at https://docs.cpuc.ca.gov/PublishedDocs/Published/G000/M451/K412/451412947.PDF.
[7] D. 22-02-004, p. 139. Available at https://docs.cpuc.ca.gov/PublishedDocs/Published/G000/M451/K412/451412947.PDF.
[8] Comments of the Southwestern Power Group and Pattern Energy on the November 18, 2021, Stakeholder Meeting in the 2021-22 Transmission Planning Process, p.1. Available at https://stakeholdercenter.caiso.com/Comments/AllComments/97a24911-d1e6-4d36-8cfe-a29d9de4e50b#org-34d425df-22df-4aa0-96cd-fcd4f02f6f2f.
[9] BPM-TPP, p. 41.
[10] “Unlike traditional utilities recovering their costs-of-service from captive and wholesale customers, investors in merchant transmission projects assume the full market risk of development.” Final Policy Statement. Allocation of Capacity on New Merchant Transmission Projects and New Cost-Based, Participant-Funded Transmission Projects. Docket No. AD12-9-000. The Federal Energy Regulatory Commission, p.2. January 17, 2013. Available at https://www.ferc.gov/sites/default/files/2020-04/E-2_36.pdf.
[11] Utility Costs and Affordability of the Grid of the Future. The California Public Utilities Commission. May 2021, p.42. Available at https://www.cpuc.ca.gov/-/media/cpuc-website/divisions/office-of-governmental-affairs-division/reports/2021/senate-bill-695-report-2021-and-en-banc-whitepaper_final_04302021.pdf.
[12] 2022 CAISO Transmission Draft Study Plan, p. 24.
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
Proposed Base Case, Sensitivity and Stress Scenario Analysis
The CAISO indicated in the 2022 Draft Study Plan and associated presentation that it will evaluate the base case and one sensitivity portfolio that the CPUC will provide for the 2022-2023 TPP.[1] The base case is designed to meet a 38 million metric ton (MMT) greenhouse gas (GHG) emission reduction target that assumes a high electric vehicle demand forecast.[2] The single proposed sensitivity portfolio is designed to meet a 30 MMT GHG emission reduction target and is still under development.[3] This year, the CAISO will also evaluate the reliability impacts with a high electrification scenario.[4]
Cal Advocates strongly supports CAISO’s plan to also conduct separate winter, summer, and spring peak studies for areas that experience high demand during these time frames historically and/or where such scenarios result in more stress on the system.[5], [6], [7] Cal Advocates also supports the CAISO’s proposal to study heavy renewable output, high load, and minimum gas generation scenarios.[8], [9]
Recommendations:
- Request that the additional sensitivities differ from the 38 MMT scenario portfolio.
Cal Advocates requests confirmation that the proposed additional sensitivities for study in the 2022 TPP will differ from the 38 MMT base case resource portfolio. In the 2021 TPP cycle, the base and sensitivity resource portfolios studied differed in the amount of out of state wind and offshore wind selected. For the 2022 TPP cycle, Cal Advocates requests that the CAISO and CPUC consider a sensitivity that selects a greater amount of at least one of the selected preferred resources in the 38 MMT portfolio such as solar plus storage to meet the 2032 state goals.
- Recommendation for a corrective action sensitivity scenario.
The proposed 38 MMT base case assumes that no corrective actions will be taken to address the expected growth in peak load over the next 10-year period. However, the implementation of corrective actions, such as time-of-use rates (TOU) and demand response programs, can put a downward pressure on load growth, and indirectly reduce the need for new transmission investment. Thus, Cal Advocates also recommends that the CAISO evaluate a scenario that evaluates the impacts of possible corrective actions to reduce anticipated growth in peak load. For example, recent findings from an Electric Power Research Institute (EPRI) electric vehicle (EV) tracking study demonstrated that TOU rates are “very effective in shifting peak loads” from EV,[10] and thus have the capacity to reduce the anticipated growth in peak load from EV.
[1] 2022 CAISO Transmission Draft Study Plan, p. 52.
[2] D.20-05-003, p. 191.
[3] D.20-05-003, p. 191.
[4] 2022 CAISO Transmission Draft Study Plan, p. 64.
[5] 2022 CAISO Transmission Draft Study Plan, p. 49.
[6] 2022 CAISO Transmission Draft Study Plan, p. 64.
[7] 2022 CAISO Transmission Draft Study Plan, p. 34.
[8] 2022 CAISO Transmission Draft Study Plan, p. 66.
[9] 2022 CAISO Transmission Draft Study Plan, pp. 38-39.
[10] Electric Vehicle Driving, Charging, and Load Shaping Analysis for Tesla Drivers: A Deep Dive Into Where, When, and How Much Salt River Project (SRP) Tesla Electric Vehicle Charge, Electric Power Research Institute, April 2019, viii.
4.
Comment on chapter 4 Economic Planning Study:
As stated in the Draft Study Plan, the CAISO intends to use the Transmission Economic Assessment Methodology (TEAM) to quantify the economic benefits of proposed transmission projects. [1] According to its Tariff, the CAISO is required to consider the degree to which, if any, the benefits of a transmission solution outweigh its costs. If a transmission solution generates a benefit-cost ratio greater than 1.0, the CAISO may conclude that its benefits outweigh its costs.
The CAISO’s TEAM framework for economic assessments requires an analysis of the effects of uncertainty on the proposed project’s expected economic benefits. This requirement recognizes that a project’s benefits may change in the future based on certain factors, including load, natural gas prices, new power plants, retired power plants, plant locations, and the future growth of the electrical network. TEAM requires a range of sensitivities to be performed as stated in Section 5 of the CAISO’s TEAM document.[2]
Sensitivity Case Selection is illustrated in CAISO’s TPP, Table 5-1: Typical sensitivity analyses. The CAISO economic analysis, thus, should not be limited to the CPUC base portfolio and the policy-driven sensitivity portfolios provided by the CPUC for study purposes. This extremely limited evaluation differs significantly from the multiple scenarios the CAISO is required to perform for sensitivity analysis under TEAM. The CAISO has placed more emphasis on careful consideration of robust baseline assumptions rather than conducting a broader range of sensitivity case studies.
Recommendation: Cal Advocates recommends the CAISO perform analysis on the entire suite of sensitivity case studies that are required for the TEAM process. In addition, the CAISO should provide details and results on the range of sensitivity case studies as required under TEAM and provide the benefit-cost ratios to stakeholders.
Rebuttable Presumption
For economic evaluations of transmission projects that may go before the CPUC for a Certificate of Public Convenience and Necessity or a Permit to Construct, Cal Advocates recommends that the CAISO Board make the findings required by D.06-11-018 with regards to the economic evaluation:
- During the TPP, the CAISO sponsors at least two meetings with an opportunity for public input and comment. The first meeting would occur sufficiently early in the CAISO’s assessment process to provide an opportunity to discuss the scope of the proposed economic assessment, including identification of the base case and other relevant assumptions, as well as resource alternatives. The second meeting would take public comment on the draft economic evaluation prior to its submission to the CAISO Board.
- The final economic evaluation that is submitted to the CAISO Board includes CAISO staff’s reasoned responses to all public comments (verbal and written) that explain how the comments were addressed in the final evaluation, either through incorporation of stakeholders’ comments in full, modification, or rejection, and the reasons, therefore.
- The public participation process has provided interested parties with sufficient time and opportunity (including sufficient access to information) to adequately review and comment on the draft TPP plan.
- The final economic evaluation meets all the requirements of D.06-11-018, as it may be amended by future Commission decisions, including the Principles and Minimum Requirements for the Economic Evaluation of Proposed Transmission Projects set forth as Attachment A to D.06-11-018.
- The final economic evaluation determines if the proposed transmission project promotes economic efficiency in that it constitutes a cost-effective upgrade to the CAISO Controlled Grid based on clearly defined information, assumptions, and weighting or combination of the relevant benefit-cost ratios and other economic criteria, including (but not limited to) difficult to quantify economic benefits, such as system operational benefits.
[1] 2022 CAISO Transmission Draft Study Plan, p. 55.
[2] The CAISO Transmission Economic Assessment Methodology, Nov 2, 2017, p. 26.
5.
Comment on chapter 5 Interregional Transmission Coordination:
The current interregional coordination process has not yet resulted in a single cost-shared project in the western interconnection[1] and is currently under FERC review.[2] However, it is still incumbent upon the CAISO to work within this process to ensure that the costs of interregional projects are allocated proportionately to the project’s beneficiaries. Of concern is the on-going consideration of the SWIP-North project for CAISO approval. This project was submitted to the CAISO, WestConnect, and NorthernGrid in March of 2016 for cost recovery.[3] The CAISO has already “voluntarily agreed to accept cost allocation [for the SWIP-north project] if the project is found to be needed by the California ISO.” [4]
If the CAISO proceeds with an approval of the SWIP-North project as an extension of the 2021-2022 TPP cycle, the cost allocation outcome would not be consistent with FERC Order No. 1000’s principle that cost allocation be commensurate with benefits.[5] LS Power, the developer of the SWIP-North project, presented the benefits of this project to NorthernGrid, but NorthernGrid has determined that this project is not needed in the current 2022 TPP cycle.[6],[7]
To address issues with the consideration of interregional projects in the western states’ interregional transmission coordination process, Cal Advocates supports the CPUC’s, Southern California Edison Company’s, and California Department of Water Resources State Water Project’s stated recommendations for improvements provided in their comments on the FERC RM21-17-000 rulemaking.[8], [9], [10]
These recommendations include: (1) requiring all regions to consider anticipated future generation in their transmission planning; [11] (2) encouraging closer alignment of benefit valuation in different regions;[12] (3) increasing the level of coordination amongst planning entities; [13] and (4) resolving any barriers to coordination through the Joint Federal-State Task Force on Electric Transmission.[14]
[1] Comments of Southern California Edison Company on FERC Rulemaking (R.) 21-17-000 on Transmission Reform, p. 4. October 12, 2021. Available at https://elibrary.ferc.gov/eLibrary/filelist?accession_num=20211012-5638.
[2] See FERC R.21-17-000 on Transmission Reform, available at https://www.ferc.gov/news-events/news/ferc-begins-reform-process-build-transmission-system-future.
[3] Southwest Intertie Project North. Overview of March 2016 ITP Submissions. Slide 8. Available at https://doc.westconnect.com/Documents.aspx?NID=17285&dl=1.
[4] ITP Evaluation Process Plan: SWP-North, p.8. June 8, 2020. Available at https://doc.westconnect.com/Documents.aspx?NID=19090&dl=1.
[5] FERC Order No. 1000. Section 587, p. 424. Available at https://www.ferc.gov/sites/default/files/2020-04/OrderNo.1000.pdf.
[6] NorthernGrid 2022 Annual Western Interregional Coordination, NorthernGrid, March 4, 2022, Slide 5.
[7] California ISO (CAISO) 2022 Annual Western Interregional Coordination Meeting, Customized Energy Solutions, March 4, 2022, p. 7.
[8] Comments of the California Department of Water Resources State Water Project, FERC Docket No. RM21-17-000, October 12, 2021, pp. 9-10.
[9] Comments of the California Public Utilities Commission, FERC Docket No. RM21-17-000, October 12, 2021, (CPUC RM21-17-000), pp. 65-70.
[10] Comments of the Southern California Edison Company, FERC Docket No. RM21-17-000, October 12, 2021, (SCE RM21-17-000, October 12, 2021) p. 3.
[11] CPUC RM21-17-000, October 12, 2021, p. 67.
[12] CPUC RM21-17-000, October 12, 2021, p. 69.
[13] SCE RM21-17-000, October 12, 2021, p. 3.
[14] Comments of the California Department of Water Resources State Water Project, FERC Docket No. RM21-17-000, October 12, 2021, p. 10.
6.
Comment on chapter 6 Other Studies:
Cal Advocates supports the CAISO’s development of a Transmission Reliability Study for the Los Angeles Basin and San Diego Imperial Valley Local Capacity Areas with reduced Reliance on Aliso Canyon Gas Storage as described on pages 63-64 of the Draft Study Plan.
7.
Please provide any additional comments:
Cal Advocates recommends that the CAISO continue to improve the TPP process, including increasing transparency and public involvement. The CAISO has publicly stated their commitment to the principle of full transparency.[1] The CASIO should respond to stakeholder comments prior to issuing the final draft TPP plan. It is important for stakeholders to know that the final draft TPP plan is informed by previous stakeholder comments.
Cal Advocates also recommends that the CAISO record all TPP meetings and post recordings in a publicly accessible location consistent with its practice for other CAISO stakeholder engagement initiatives and workshops. TPP meetings provide important information and serve as the only engagement platform for stakeholders. All TPP meetings should also be recorded for stakeholders who cannot attend at the specific time and published for public accountability. There is no technological or logical barrier to Cal Advocates’ recommendation because the CAISO already records and publishes other workshops or stakeholder engagement events.
To provide adequate time for stakeholders to evaluate proposed reliability, policy, and economic projects in the CAISO TPP, as we specified in our comments on the 2021-2022 TPP, more than two weeks should be provided for stakeholder comments. Cal Advocates recommends a minimum of three weeks for stakeholder review consistent with CPUC’s stakeholder engagement policies. For example, the CPUC public process allows for more than two weeks to file a protest or response. According to the CPUC Rules of Practice and Procedure, California Code of Regulations Title 20, Division 1, Chapter 1, section 2.6, parties may file a protest or response within 30 days from when the application appears on the Daily Calendar. Or according to CPUC General Order 96-B, section 7.4.1, parties have 20 days to protest or respond to an advice letter from when it is filed.
To this end, Cal Advocates recommends the following changes to the CAISO Tariff Section for the Transmission Planning Process (TPP) and the BPM for the TPP.
Recommended Changes to CAISO Tariff, Section 24 Comprehensive Transmission Planning Process Tariff
Section 24.4.9
Interested parties will be provided a minimum of a two (2) three (3) week period to provide written comments regarding the technical study results and the proposals submitted by the Participating TOs [Transmission Owners].[2]
Recommended Changes to CAISO Business Practice Manual for the Transmission Planning Process
4.2 Technical Study Results: Posting and Presentation
Stakeholders must submit comments on the topics covered during this stakeholder meeting within three two weeks of the meeting. Once the CAISO has reviewed the comments, the CAISO will post responses to the stakeholder comments and the final study results.[3]
[1] California State Legislature, State Assemble Committee on Utilities and Energy, Mid-August Heat Storm Joint Preliminary Report by California Energy Commission, California Public Utilities Commission, California Independent System Operator, October 12, 2020. Statement from CEO Elliot Mainzer.
[2] California Independent System Operator Corporation Fifth Replacement FERC Electric Tariff, Section 24, Comprehensive Transmission Planning Process, September 9, 2020, Section 24.4.9.
[3] BPM-TPP, p. 32.
CEERT, EDF
Submitted 03/16/2022, 11:01 am
Submitted on behalf of
CEERT, EDF
1.
Comment on chapter 1 Introduction:
California’s clean energy economy is going to need clean energy infrastructure. To power our homes and vehicles with renewables, we’re going to need to build a lot of solar and wind, geothermal – and we’re going to need transmission infrastructure to deliver it to customers and maintain a reliable grid. The Public Interest Organizations Center for Energy, Efficiency and Renewable Technologies (CEERT), Environmental Defense Fund (EDF)appreciate the opportunity to comment and the promoted timeline to participate in various stages of the development of the 10-year 2022-2023 transmission planning process.
As mentioned in earlier comments:
- We recommend CAISO and CPUC use the 30 MMT target since the Governor directed the agencies to consider adoption of more stringent GHG targets.
- We appreciate the coordination but the models, procurement policies and planning must be better integrated with each agency to ensure consistent, efficient, and effective implementation of policies to meet SB 100 requirements. The PIOs support the recommendation by CAISO staff for the transmission upgrades (including strengthen the 230kV to 500kV reconducting) and the inclusion of new lines needed for the Base and additional Portfolios.
- Short- and long-term planning components must be amalgamated to avoid taking too many small steps to fix all the needs. More in-depth analysis on how and when a larger project could be more cost effective over time while also addressing reliability and public policy needs. The PIOs support the recommendations for the transmission upgrades identified for the Base Portfolio in the off-peak assessment if they are found to be affordable and or meet public policy requirements.
- As the CAISO performs further evaluation of transmission alternatives to identify the preferred solutions including updates to the production cost modeling, it is imperative to incorporate all renewable energy targets looking at economy wide decarbonization for local and system wide needs.
- We recommend a stronger integrated analysis to address the current disconnect between the enormous scale of renewable energy generation build needed with new and upgrades to the transmission system in the next -5-10 and 15 years and the current short-term view that can cost California millions of dollars.
2.
Comment on chapter 2 Reliability Assessment:
Regarding Extreme Events, Requirement R4.5 of the NERC Standard requires that extreme events that are “expected to produce more severe System impacts” are solved through transmission planning, so it would be prudent for CAISO to consider both reliability and public policy options to address extreme event risk mitigation and highlight in upcoming stakeholder meetings.
Also, CAISO should consider implications of the transmission plan for changes to assumed transmission line ratings to reflect FERC 2021 ruling. Given potential wholesale energy market offerings to be available in the West and the recent FERC rulings on transmission ratings modeling and impacts to transmission availability, there could be long-term impacts to transmission planning for interregional investments and line rating capacity should be discussed in stakeholder forums.
The PIOs support the base scenarios adapting to include more summer and winter peak inputs for 2032 and encourage additional study areas to the four mentioned.
This reliance on the reliability case for the policy-driven base case does not benefit the state in better understanding how to meet it climate goals by 2032.
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
As the base portfolio, the CPUC transmitted a PSP portfolio based on the 38 MMT GHG target by 2030 and the 2020 IEPR demand forecast utilizing the high electric vehicle assumptions.
The PIOs strongly urge the CPUC and the CAISO to support the staff development of a policy-driven sensitivity portfolio in consultation with the CEC and CAISO based on a 30 MMT GHG target, and associated busbar mapping.
The PIOs support the necessity of the 30 MMT GHG target as a portfolio for inclusion.
As the CAISO and the CPUC collaborate on new policy-driven transmission upgrades associated specifically with storage mapping in this planning cycle, and when storage resources are required for mitigation of transmission issues identified in the CAISO’s 2021-2022 Transmission Plan, the coordination also includes stakeholder input to help guide the adjustments in the CPUC’s mapping of storage resources to allow for the inclusion in the CAISO’s analysis of the 2022-2023 TPP portfolios.
As noted, the BTM-PV will be modeled explicitly in the 2022- 2023 TPP base cases, and we agree with the 2021 IEPR data source.
4.
Comment on chapter 4 Economic Planning Study:
Since all three FERC 1000 regions in the west will use the WECC ADS 2032 production cost model, it would be beneficial to update stakeholders on any significant regional changes as well as advancement of interstate transmission lines.
And as the CAISO receives other model updates that would be also needed through the PCM development and validation process, including stakeholders is critical to advancing support for model outcomes and projects.
The PIOs support the CAISO carrying requests forward as potential high priority study requests, which are mainly based on the previous cycle’s congestion analysis and provides more opportunity for study requests to consider the latest and most relevant information available.
5.
Comment on chapter 5 Interregional Transmission Coordination:
Facilitating trade between and among regions is a critical part of the clean energy transition, and it’s important to recognize contributions in all directions – access to abundant wind resources helps California manage reliability, while California’s abundant solar and wind resources provide huge economic and environmental benefit to the whole region especially when partnered with storage.
In the recent March 4th interregional planning meeting, there are reliability, public policy, and economic links across the broader western grid. As the west moves to more interconnected inclusive transmission planning ensuring benefits and costs can be shared fairly by customers across the west.
6.
Comment on chapter 6 Other Studies:
As noted in the report and presentation, the 20-year Transmission Outlook must have clearly understood feedback loops to the 10-year transmission plans and clear expectations of what is needed. It is also important to identify gaps in planning and ways to adapt to meet the reliability and public policy requirements. The PIO/CEAs worry there will be gaps and continued piecemeal approaches taken if clear steps to build transmission are not outlined to match agency roles and responsibilities.
It is essential to continue an open dialogue on the ongoing findings and updates to the SB 100 processes and strongly encourage additional stakeholder sessions to collect additional insights and parameters refining future outlook development 10-year plans. How will the CAISO review the previous canceled and on-hold projects that could benefit the 10-year analysis and may have altered and improved since the last review?
As the CAISO and CPUC continue to build on collaboration, the PIO/CEAs ask that restrictions limiting data sharing and confidentiality requirements be worked out sooner than later to avoid delays.
As identified in earlier comments, we strongly urge the CAISO to move these upgrades forward as a critical first step.
Upgrades recommended for current TPP cycle:
- Antelope/Vincent line rating increase
- Colorado River No. 3 transformer
- Reconductor Lugo-Victor 230
- San Diego Internal Constraint
- Silvergate-Bay Blvd Series Reactor (LCR benefit?)
- Tesla-Westley 230 kV
- El Dorado 500/230 Transformer #5
- GLW-VEA Area Constraint
The following recommended upgrades were included in the Base Case scenario in D.21-02-008 (46MMT) but have not yet been approved in the TPP.
- Gates 500/230kV transformer bank #13 (will be included in current TPP)
- Gates-Cal Flats 230kV line reconductor (identified by CAISO)
- Eldorado 500/230 kV 6AA transformer bank (will be included in current TPP)
- Whirlwind 500/230kV transformer bank (will be included in current TPP)
- Lugo 500/230kV 3AA transformer bank (identified by CAISO)
o We recommend adding the associated Victor-Lugo constraint to expand access projects to the north
Examine alignment of the CAISO transmission planning processes, CPUC integrated resource planning, and LSE procurement activities to ensure use of best available information for decision making.
7.
Please provide any additional comments:
The PIOs look forward to participating in the development of the high electrification scenario before the June 2022 release date.
The PIOs also looks forward to participating in the Reduced Reliance on Aliso Canyon Gas Storage Special Study and asks the CAISO and CPUC to also work closely with all the balancing authorities in CA.
Again, the PIOs support the necessity of the 30 MMT GHG target as a portfolio for inclusion.
We also recommend
- Equity needs to be included in updated portfolios and attention to health and well-being of local impacted communities is essential
- Ensuring that the CPUC provides updated guidance and scenarios to the CAISO to plan and approve sufficient transmission for the 11,500 NQC MW of new capacity identified in the recent IRP Proposed Decisions.
- Studying long-lead time resources, including offshore wind, long-duration storage, and green hydrogen, in the IRP and TPP, and tie the outcomes of the CAISO’s 20-year transmission outlook into procurement activities.
- Adding additional sensitivities retiring the gas plants by 2035 and use the 30MMT GHG targets.
- Incorporate climate impacts and reliability assessments into near-, mid- and long-term planning studies.
- Continue to coordinate and make transparent the planning processes; IEPR, IRP, TPP and Scoping Plan to achieve SB 100 goals and support grid reliability.
The PIOs greatly appreciate the opportunity to comment. Transmission infrastructure is an investment where actual costs to customers are much more modest when considering the value and longevity of these transmission projects. It is important to plan in coordinated and inclusive way and build equitably and accordingly.
Thank you,
V. John White
Executive Director
Center for Energy Efficiency and Renewable Technologies
www.ceert.org
Michael Colvin
Director Regulatory and Legislative Affairs, California Energy Program
Environmental Defense Fund
www.edf.org
Friends of Minidoka
Submitted 03/14/2022, 02:39 pm
Submitted on behalf of
Friends of Minidoka
1.
Comment on chapter 1 Introduction:
Thank you for the opportunity to submit comments regarding the 2022-2023 Transmission Planning Process (TPP) Draft Study Plan and CPUC Modeling Assumptions.
The Friend of Minidoka is an Idaho non-profit corporation and official “friends” group of the National Park Service (NPS). We appreciate the opportunity to provide CAISO with information to support its decision-making regarding transmission planning for Out-of-State (OOS) Idaho wind.
The Friends of Minidoka’s mission is to support public education and the preservation of the Minidoka National Historic Site (NHS), a unit of the National Park System located in southern Idaho.
The Minidoka NHS site is sacred to Japanese Americans. It preserves the memories and tells the stories of Japanese American people who were wrongfully incarcerated during World War II.
The Friends of Minidoka plan to participate in various forums, including CAISO's TPP, to express its support for maintaining the integrity of the Minidoka National Historic Site's fundamental resources and values as a place for learning and healing. FOM also plans to express its concerns about the racial justice impacts of the Lava Ridge Wind Project, which LS Power plans to connect to its proposed Southwest Intertie Project-North (SWIP-N).
The National Park Service has described how the Lava Ridge Wind Project will adversely impact the Minidoka National Historic Site:
“…the Lava Ridge Project would fundamentally change the psychological and physical feelings of remoteness and isolation one experiences when visiting Minidoka NHS, as the lands north would be transformed into a large-scale renewable energy site marked by hundreds of wind turbines, transmission towers and associated ancillary infrastructure. Approaching the site and walking its grounds, visitors would no longer experience the feeling of a rural, undeveloped landscape recalling what Minidoka was like during World War II.”
In 1942, the U.S. Government sited the Minidoka Relocation Center near a railroad line to transport U.S. citizens of Japanese descent from Assembly Centers located in California, Oregon and Washington State.
Today, the railroad line parallels several east-west transmission lines in southern Idaho. Minidoka is located near Midpoint, Idaho, which is the proposed northern terminus of LS Power’s SWIP-N line. Along with other projects, the SWIP-N line would connect LS Power’s proposed Lava Ridge and Salmon Falls, Idaho wind projects to Robinson Summit, Nevada and the California grid via the ON Line-DesertLink (Eldorado).
FOM is concerned that the Lava Ridge Wind Project would negatively impact Minidoka, which was added to the National Register of Historic Places in 1979.
In 1986, the Bureau of Land Management (BLM) issued the Monument Resource Management Plan for the federal lands now proposed for the Lava Ridge Project. This plan is thirty-six years old.
In 1994, the BLM issued a record-of-decision for the SWIP-N right-of-way, which routed the line through the middle of the Minidoka NHS. BLM’s environmental impact statement and NEPA compliance for the SWIP line is 28 years old. Despite the fact that the Lava Ridge Wind Project would connect to SWIP-N, the BLM has not analyzed the environmental impacts of these two projects as connected actions under the National Environmental Policy Act (NEPA).
In 2001, President Clinton designated Minidoka as a National Monument, and unit of the National Park System. The National Park Service is required by the Organic and Redwoods Acts to manage the park unimpaired for future generations.
In 2005, the BLM completed its Wind Energy Development Programmatic EIS, which found that the site proposed for the Lava Ridge project has “low” wind energy potential.
In 2008, the U.S. Congress passed bipartisan legislation to expand and redesignate the park as the Minidoka National Historic Site.
In 2009, LS Power/Great Basin Transmission approached NPS to seek approval for the SWIP-N right-of-way that would have cut the Minidoka National Historic Site in two. Following NPS objections, the Department of the Interior relocated the line away from the Historic Site.
As part of President’s Biden’s Fiscal Year 2022 budget request to Congress, last year, the Department of the Interior proposed a budget increase for Minidoka NHS, as part of its commitment to underserved communities. https://www.doi.gov/news/statement-secretary-haaland-presidents-fy22-discretionary-funding-request
In August 2021, NEPA and other federal laws, the BLM announced the beginning of the public scoping and EIS process for the proposed Lava Ridge Wind Project, which includes 400 wind turbines, as tall as 740 feet. LS Power proposed to site the closest turbines within two miles of the park visitor center and on the historic footprint of the Minidoka Relocation Center. According to NPS, 340 turbines would be within the viewshed of the Minidoka National Historic Site and create a visual wall of towers that would occupy about one third of the park’s 360 degrees of viewshed.
In 2022, the BLM issued a summary of public comments received during the NEPA scoping process. These comments included opposition to the project based on impacts on the Japanese American community, treaty rights held by the Shoshone Bannock Tribes, visual impacts on historic sites and cultural resources, impacts to big game migratory corridors and winter habitat, impacts to bat and bird populations, potential conflicts with current livestock operations, negative effects to dispersed recreation opportunities, loss and fragmentation of sage grouse habitat, damage to local road systems, opposition to potential for a large non-local workforce and concerns about negative health effects. Some commenters supported the project’s potential for new jobs.
In October 2021, the California Public Utilities Commission (CPUC) issued a draft Environmental and Social Justice Action Plan (version 2.0), which included the following Goal and Objectives:
“Goal 1: Consistently integrate equity and access considerations throughout CPUC regulatory activities.
REVISED OBJECTIVES: 1.1 Build Systematic Approaches for ESJ Priorities: Continue building systematic approaches for considering ESJ issues in proceedings and decisions, as well as implementation processes included in advice letters, general orders, and resolutions. Build understanding of critical ESJ concepts and definitions to ensure alignment and deepen impact.”
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
The Friends of Minidoka encourages CAISO to consider including CPUC ESJ Action Plan goals, once finalized, in its transmission planning analysis as policy goals.
The Draft Study Plan includes Table 3.3-1, which shows “the new resource buildout of 38 MMT Core with 2020 IEPR Demand and High EV Penetration (Cumulative MW)”
Table 3.3-1: New Resource Buildout of 38 MMT Core with 2020 IE includes a line for Resource Type: “Wind on New Out-of-State Transmission,” 1,500 MW.
Regarding the Lava Ridge and SWIP-N projects, the Friends of Minidoka recommends that CAISO consider CPUC’s ESJ Action Plan in the 2022-2023 TPP. The CAISO should also consider the status and timing of the federal and state permitting decisions and approval processes relating to Idaho wind generation and transmission.
4.
Comment on chapter 4 Economic Planning Study:
No comments
5.
Comment on chapter 5 Interregional Transmission Coordination:
No comments
6.
Comment on chapter 6 Other Studies:
No comments
7.
Please provide any additional comments:
CPUC’s Modeling Assumptions includes Table 26, entitled “Final mapping results summarized by RESOLVE resource type.” Table 26 includes an entry for “Wyoming Idaho – Wind OOS.”
Regarding the Lava Ridge and SWIP-N projects, the Friends of Minidoka recommends that CAISO consider CPUC’s ESJ Action Plan in the 2022-2023 TPP. The CAISO should also consider the status and timing of the federal and state permitting decisions and approval processes relating to Idaho wind generation and transmission.
As our nation marks the 80th anniversary of the forced incarceration of Japanese Americans from California, we wanted to share Governor Newsom’s 2022 Day of Remembrance Proclamation:
“Over two and a half years, the U.S. government removed Japanese Americans from their homes on the West Coast – without a trial or due process – forcing them into concentration camps in unfamiliar lands. Uprooted from their lives and livelihoods, they endured miserable conditions and treatment by military guards.
Despite these experiences, thousands of young Japanese-American men enlisted in the U.S. armed forces, bravely fighting to defend the nation that was abridging their own freedoms at home. We honor their sacrifice, as well as the resilience that made it possible for thousands of Japanese-American families to reclaim and rebuild their lives after the war.
A decision motivated by discrimination and xenophobia, the internment of Japanese Americans was a betrayal of our most sacred values as a nation that we must never repeat. This stain on our history should remind us to always stand up for our fellow Americans, regardless of their national origin or immigration status, and protect the civil rights and liberties that we hold dear.”
Thank you for considering our comments. We would be pleased to answer any questions or provide additional information.
North Gila - Imperial Valley #2 Project
Submitted 03/14/2022, 01:04 pm
Submitted on behalf of
NGIV2 LLC, Grid United LLC, IID, Citizens Energy Corporation
1.
Comment on chapter 1 Introduction:
NGIV2, LLC appreciates the opportunity to provide comments on the CAISO’s draft 2022-2023 Transmission Planning Process (“TPP”) Study Plan. NGIV2, LLC is also submitting an Economic Planning Study Request, herewith, to the CAISO for the 2022-23 Transmission Plan. The request is for the CAISO to perform an economic analysis of its North Gila-Imperial Valley #2 (“NGIV2”) transmission project at a cost of $271M to the CAISO, revising certain assumptions for the production cost models, and considering other multi-value benefits provided by the project, including potential partial ownership in the project by the Imperial Irrigation District (“IID”). We believe that the addition of the North Gila – Imperial Valley #2 Project will play a key role in meeting the broader reliability, policy and economic benefits, as well as additional transmission capacity for the region. Specifically:
- NGIV2 is a multi-value transmission project providing economic, reliability and policy benefits for the regional transmission system.
- Provide an incremental 1000-1250 MW of transmission capacity for the delivery of renewable resources (geothermal and solar) from Arizona and the Imperial Valley.
- Increases the reliability and decreases the reliance of remedial action schemes for the broader San Diego/Imperial Valley region for loss of the existing North Gila – Imperial Valley 500 kV line.
- Reduces carbon emissions by decreasing the San Diego area reliance on local gas capacity by as much as 865MW.
- Reduces the congestion on the existing North Gila – Imperial Valley 500 kV line.
- Unlocks stranded capacity west of North Gila under normal and contingency conditions.
The current estimated timeframe for the North Gila – Imperial Valley #2 Project to be in-service is December 2026 would allow the Project Sponsors to potentially receive funds from the Infrastructure Investment and Jobs Act and provide further cost improvements.
2.
Comment on chapter 2 Reliability Assessment:
WECC Path Re rating request due to change in reliability criteria
Several Path owners have expressed interest in re-rating Paths due to the change in reliability criteria around multiple lines in a common corridor. Specifically, the following are proposed to be re-rated:
|
Existing Rating
|
Proposed Rating
|
Path 15 - Midway – Los Banos
|
2,000 - 3,265 MW North to South
|
3,700 MW - 4,600 MW North to South
|
Path 17 - Borah West
|
2,557 MW East to West
|
2,800 MW East to West
|
Path 26 - Northern – Southern California
|
3,000 MW South to North
4,000 MW North to South
|
4,400 MW South to North
5,000 MW North to South
|
Path 66 – California Oregon Intertie (COI)
|
4,800 MW North to South
|
5,100 MW North to South
|
As evident from past studies, most of these paths are often times the congested elements. While the path re-rating studies have not been completed, we request that CAISO perform sensitivities on some, if not all paths that could have an impact on the regional analysis.
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
Imperial Valley Geothermal MW, Bus Bar Mapping and Dispatch
CAISO’s draft 2022-2023 Study Plan presentation slide 57/86 ‘Non Storage resources by location’ shows only 600 MW of geothermal when compared to 700 MW shown in Table 14, pg. 46/67 of the CPUC Staff Report Attachment A: Modeling Assumptions for the 2022-2023 Transmission Planning Process filed December 22, 2021. Can you please explain if this is intentional?
The CPUC report on the Modeling Assumptions for the 2022-2023 Transmission Planning Process also note the following in Section 7.5 Transmission Implications of the Final Mapped Portfolio on pages 58 and 67:
Thus, although the 700 MW of geothermal resources mapped to the Bannister substation within the Imperial Irrigation District’s (IID’s) BAA are unlikely to require any upgrades within the CAISO transmission system, assuming the resources interconnect with the CAISO to the north in the Riverside area, the impacts on the IID’s system are unknown, as are the type and cost of any upgrades that may be required to successfully interconnect the resources to deliver to the CAISO.
Can CAISO please comment on why the geothermal resources are assumed to interconnect with CAISO to the north in the Riverside area? As described in the following Economic Study Request for NGIV2 project, we believe our project would provide a connection into CAISO through the new 500/230 kV Dunes Substation that connects into IID’s 230 kV Highline Substation. We request CAISO to consider moving geothermal resources to interconnect to the IID system with an opportunity to deliver to the CAISO at Imperial Valley, Mirage/Devers and the new Dunes Substation.
4.
Comment on chapter 4 Economic Planning Study:
High Priority Economic Study Request for the North Gila – Imperial Valley #2 Project
On behalf of the project sponsors, NGIV2 LLC, Citizens Energy Corporation, Grid United LLC, and the IID, we are pleased to submit the North Gila – Imperial Valley #2 Project (“NGIV2”) to the CAISO for consideration as a high-priority economic study request in the 2022-2023 Transmission Planning Process. Collectively, the project sponsors propose to have 80% of the 500kV line costs recovered via a CAISO PTO, at a cost of $271M, and the remaining 20% via the IID transmission tariff. The NGIV2 Project will create an opportunity for a new CAISO delivery point at the proposed Dunes 500 kV substation, reduce Local Capacity Requirements (“LCR”) for the greater Imperial Valley/San Diego region, and provide a major import and export transmission path with an incremental 1,250 MW of capacity to deliver both In-State solar and geothermal resources from the Imperial County, and out of state resources, particularly wind resources delivered from the Palo Verde Hub. Lastly, the NGIV2 Project will provide additional transmission capacity for the IID for their stranded capacity at North Gila from the Hassayampa – North Gila #2 (“HANG2”) 500 kV line.
Project configuration
The 85 mile long North Gila – Imperial Valley #2 Project is a new 500 kV line generally paralleling the existing North Gila – Imperial Valley #1 500 kV line (also known as the Southwest Power Link, or “SWPL”).
For this submittal as a high-priority economic study request by the CAISO, the Project Sponsors propose the following project facility additions:
- A new 500 kV termination at the existing CAISO North Gila 500 kV Substation (operated by APS).
- A new 85-mile, 500 kV line between the North Gila 500 kV Substation to the Imperial Valley 500kV Substation. While the IID is proposing to be a 20% owner in this line, the remaining 80% is to be owned and costs recovered by a CAISO PTO.
- A new 500 kV termination at the existing CAISO Imperial Valley 500KV Substation (operated by SDGE).
- Contingent Facilities: Series compensation located at a proposed intermediate substation (known as Dunes), located approximately 56 miles west from North Gila, the location is electrically near the IID Highline 230 kV Substation. Note that the existing North Gila – Imperial Valley #1 line includes 50% series compensation, but is currently operated bypassed. The cost of these contingent facilities are included in the cost of the NGIV2 Project.
Facilities to be owned and operated by the IID:
- A new 500 kV termination at the 500 kV Dunes Substation (initially only a contingent series compensation station) for the termination of a 1120 MVA 500/230 kV transformer.
- New Dunes 230 kV Switching Station.
- A new 6.6-mile, 230 kV segment from the 230 kV Dunes Switching Station terminating into IID’s existing 230 kV Highline Substation. IID will Own 100% and operate the Dunes 500/230 kV transformer and the 230 kV transmission line between Dunes and Highline substations.
Figure 1 represents a simplified single-line diagram of the proposed facilities and ownership.
Figure 1: Simplified Single Line Diagram of the North Gila – Imperial Valley #2 Project Facilities
NGIV2 has an Accepted Rating via the WECC Path Rating Process
The NGIV2 project has completed Phase 2 of the WECC Path Rating Process and has been granted an Accepted Rating for an incremental 1,250 MW of transfer capability on the West of Colorado (“WOR”) or Path 46, increasing the Path 46 rating from 11,200 MW to 12,450 MW. The Hassayampa- North Gila #2 Project is now in-service but limited to only 500 MW of scheduling capability, with an incremental 100 MW planned with the addition of the Arizona Public Service’s (“APS”) 230 kV Orchard Project. Refer to Figure 2 for the facilities that make up the WECC Path 46 or WOR.
Project Cost Sharing with Imperial Irrigation District Participation
IID has submitted a conceptual project into the WestConnect transmission planning process consisting of approximately 60 miles of new 230 kV transmission line and associated facilities between North Gila and Highline 230 kV substations, at a cost of approximately $140M to meet IID’s resource and load serving obligations. However, the proposed NGIV2 Project configuration fulfills IIDs expected future needs, provides several benefits to the CAISO ratepayers, and furthers the State of California’s SB100 and Imperial County’s policy goals (Imperial County Lithium Valley Economic Opportunity Investment Plan’ (“LVIP”)1. Therefore, IID proposes to participate with the NGIV2 Project co-sponsors to allocate 100% of the cost of 230 kV facilities i.e., the 230 kV Dunes to Highline 6.6-mile segment, including the Dunes 500/230 kV transformer and approximately 20% of the cost of the 500 kV facilities to IID tariff. The remaining 80% of the costs of the 500 kV facilities are proposed to be recovered via a CAISO PTO. Please note for the total NGIV2 project cost, this amounts to an approximate cost split of 20% (IID) / 80% (CAISO). Based on the past CAISO evaluations and before considering any benefits that will be assessed in the upcoming 2022-2023 TPP, we expect the Project with its reduced cost, CAISO ratepayers will be found to meet CAISO’s economic and policy criteria. NGIV2 project sponsors want to highlight that the project is NOT requesting Interregional Cost Allocation and request that CAISO evaluate the project to fulfill its own regional transmission needs as described previously and similar to the Delaney to Colorado River, Harry Allen to Eldorado, and SWIP North projects. The Project Sponsor proposes that the CAISO be the BAA for the 500 kV transmission line facilities (including the contingent series compensation facilities).
CAISO Policy Benefits
We understand and acknowledge that assessing and quantifying all the benefits that a proposed 500 kV transmission project might offer in the future based on current assumptions is very challenging, especially with the ever evolving and increasingly complex grid. However, CAISO’s tariff Section 24.4.6.6 notes that “CAISO will determine the need for, and identify such policy-driven transmission solutions that efficiently and effectively meet applicable policies under alternative resource location and integration assumptions and scenarios, while mitigating the risk of stranded investment”2. We strongly believe the risk of NGIV2 becoming a stranded asset is minimal to zero because of a) its strategic location in Imperial County with access to both in-state and out-of-state renewable resources through the Palo Verde Hub and b) tremendous commercial interest as evident from the CAISO, IID, and APS generation queues and documented potential for load growth in the San Diego - Imperial Valley
- CEC Docket no: 20-LITHIUM-01, Document Title: Lithium Valley Economic Opportunity Investment Plan (Imperial County LVIP),TN# 241584, Docketed Date: 02/18/2022 https://efiling.energy.ca.gov/Lists/DocketLog.aspx?docketnumber=20-LITHIUM-01
- https://www.caiso.com/Documents/Section24-ComprehensiveTransmissionPlanningProcess-asof-Sep9-2020.pdf
Hence, we request that in addition to the economic benefits that can be practically quantified, CAISO also consider the policy and long-term benefits that such a strategically located transmission line would provide to meet both the current 2022-2023 Transmission Plan’s base portfolio target of 38 MMT GHG emissions and California’s SB100 goals in the longer term.
Regional Public Policy Benefits of NGIV2
In addition to being a step towards the State of California’s SB100 goals, as noted previously, we also wanted to stress both local county level and national public policy benefits of NGIV2. As stated above commercial interest in both geothermal generation and lithium extraction in the Salton Sea area has exploded. In addition to the potential for geothermal production between 1500-3000 MW over the next 10-15 years, Imperial County staff also estimate that the county may hold as much as 15 MMT of lithium in addition to other rare earth materials. NGIV2, therefore, has a direct impact on ramping up new development in the area and creating economic growth and job opportunities for a Disadvantaged Community. Due to the forecasted demand for electric vehicles, Battery Energy Storage Systems (“BESS”), and other electronic devices, access to lithium and rare earth resources is also widely considered key to the National Security Interests of the United States.
Local Capacity/Resource Adequacy Benefit
As noted above, based on CAISO’s evaluation of NGIV2 in the 2018-2019 TPP3, the project is expected to provide more than 865 MW reduction in LCR in the San Diego-Imperial Valley area with the net present value of the savings calculated to be more than $329M. We request CAISO to please refresh this analysis with the latest resource plan and topology assumptions including the NGIV2 Project.
Production Cost Benefit
Similar to the LCR benefits, we are confident that the trend of production cost benefits (or net CAISO load payment savings) realized from the project as summarized in Section 5.7.5 of the 2013-2014 TPP4 and Section 5.4.1.3 of the 2018-2019 TPP3 will continue due to increased use of more efficient resources in the Imperial Valley, Arizona Public Service (“APS”), Palo Verde trading Hub and Salt River Project (“SRP”), displacing more expensive generation in Southern California.
We would also like to note that the existing North Gila – Imperial Valley #1 transmission line, SWPL, has consistently shown up as a congested element in CAISO’s TPP in recent years including both the 2021-2023 TPP and even in the 20-year Transmission Outlook Study.
Integration & Deliverability of geographically diverse Renewable Resources including Out of State Wind from the Palo Verde Hub
The NGIV2 Project will be a major transmission expansion between the Southern Arizona area and Southern California area. As noted above, it has already been granted a WECC Accepted Path Rating that adds 1,250 MW incremental transfer capability to the WOR Path, or WECC Path 46, increasing the interregional transfer capability between Arizona and California, specifically between the Palo Verde hub and load centers in Southern California.
In addition to the In-State solar and geothermal additions enabled by the project, we also request CAISO consider the integration and deliverability potential for geographically diverse Out of State solar and wind, especially the 438 MW of New Mexico wind included in the current 2022-2023 TPP Base Portfolio proposed to be delivered at Palo Verde. Although not part of the current study plan, we implore CAISO to reexamine the Out of State wind study conducted as part of the 2021-2022 year TPP which included 1,500 MWs of New Mexico wind at Pinal Central (CAISO Palo Verde Hub). We believe the incremental 1,250 MW of WOR path rating achieved by NGIV2 would provide better production cost and deliverability to Southern California load than what was achieved in the 2021-2022 TPP analysis.
Local Gas Fired Generation Reduction Benefit
In the recent years the CPUC and CAISO have had to balance the reliability needs of local inefficient gas units against its associated GHG emissions. CAISO noted in the Draft 2021-2022 TPP pages 335 and 391 “In particular, the longer-term requirements for gas-fired generation for system and flexible capacity requirements continue to be examined, in the CPUC’s integrated resource planning process, but actionable direction regarding the need for these resources for those purposes is not yet available”. CPUC staff noted in Section 6 of the CPUC Staff paper published on October 2021 titled “Considering Gas Capacity Upgrades to Address Reliability Risk in Integrated Resource Planning”8 that “ Further, to shed light on related, long-term questions regarding the CAISO gas fleet, the next IRP cycle could study the existing fleet and emerging technologies in more detail. This could provide more insight into the appropriate role of the gas fleet in moving towards a decarbonized electricity system. As one example of potential work to support this, the IRP could explore an expansion of its system and local reliability modeling capabilities to further consider when storage technologies or emerging technology resources may economically displace gas generators from their local capacity provision”.
NGIV2 project sponsors want to note that the Salton Sea region of California is home to some of the best untapped geothermal resources in the country. We appreciate that the CPUC and CAISO have included 700 MW of geothermal mapped to the Imperial Valley area in the current base portfolio. However, Imperial County staff, who are much closer to gauging actual commercial interest in geothermal and lithium extraction development within the county, expect between 1500-3000 MWs of geothermal in the next 10-15 years as stated in the ‘Imperial County Lithium Valley Economic Opportunity Investment Plan (“LVIP).’1
- https://www.cpuc.ca.gov/-/media/cpuc-website/divisions/energy-division/documents/integrated-resource-plan-and-long-term-procurement-plan-irp-ltpp/2019-2020-irp-events-and-materials/cpuc-gas-upgrades-staff-paper-october-2021.pdf
With IID’s intention for an interconnection between the NGIV2 Project into IID’s 230 kV Highline Substation would provide an additional parallel path to the IID 230 kV “S” line project interconnection from IID’s El Centro 230 kV to Imperial Valley 230 kV substations to enable dispatchable renewable FCDS Geothermal to reduce reliance on local gas fired generation in the San Diego – Imperial Valley area. A future 500 kV interconnection between Dunes – Midway - Devers could also potentially provide similar benefits in the LA basin and the region.
Reliability Benefits of NGIV2
The NGIV2 project would increase the reliability benefits for the CAISO, IID and broader southern WECC area for loss of the existing North Gila - Imperial Valley #1 500 kV segment of the Southwest Power Link (“SWPL”) line. While the primary focus of this high-priority economic study request to the CAISO for the NGIV2 Project, the Project Sponsors request the CAISO to also consider the invaluable operational flexibility, potential elimination or substantial reduction of existing Remedial Action Schemes (RAS’s”) in the San Diego and Imperial Valley areas, operating reserve requirements, and frequency reserve margins that might be achieved by the addition of the NGIV2 Project.
Comments on CAISO economic modeling assumptions and methodology
We request CAISO to consider these specific comments and assumptions as it relates to the NGIV2 Project high-priority economic study request.
- Include an incremental 1,250 MW transfer capability on WECC Path 46, or the WOR Path, for the post-project NGIV2 Project case bringing the target flows from the existing 11,200 MW to 12,450 MW as per the Accepted Rating in the WECC Path Three Rating Phase Process. The confidential GE PSLF model data has been submitted to the CAISO regional transmission email.
- Include $271M as the Capital Cost of the Project to be allocated via a CAISO PTO.
- Include the review of the San Diego/Imperial Valley LCR reduction benefit analysis with the inclusion of the NGIV2 Project along with other economic analysis that CAISO performs.
- As per our comments on the draft 2022-2023 Study Plan, several Path Owners have requested Re- Rating due to a change in reliability criteria around common corridor contingencies. We request the CAISO perform a sensitivity for the NGIV2 Project with at least the proposed Path 26 rating of 4,400 MW South to North and 5,000 MW North to South
In conclusion, we believe the NGIV2 Project Economic study request fulfills the parameters set forth in CAISO’s tariff Section 24.3.4.1 (b)(c)(d)(e) “CAISO Assessment of Requests for Economic Planning Studies” and request CAISO include NGIV2 as a high priority Economic Study Request in the 2022-2023 TPP. The NGIV2 Project sponsors thanks the CAISO for considering these study comments and the associated request to study the NGIV2 Project. We look forward to working with CAISO staff on the 2022- 2023 TPP.
5.
Comment on chapter 5 Interregional Transmission Coordination:
We appreciate the CAISO participating in the Interregional Transmission Coordination efforts.
6.
Comment on chapter 6 Other Studies:
As noted above, the NGIV2 Project is expected to provide a reduction in LCR in the San Diego-Imperial Valley area, specifically for the 2027 assessment. We request that the NGIV2 Project be included as a sensitivity to the special study of the reduced reliance of the Aliso Canyon Gas Storage facility.
7.
Please provide any additional comments:
The project sponsors of the North Gila - Imperial Valley #2 Project appreciates the CAISO for their review of the project as a part of the 2022-2023 Transmission Planning Process.
We reiterate that the addition of the North Gila – Imperial Valley #2 Project will play a key role in meeting the broader reliability, policy and economic benefits, as well as additional transmission capacity for the region. Specifically:
- NGIV2 is a multi-value transmission project providing economic, reliability and policy benefits for the regional transmission system.
- Provide an incremental 1000-1250 MW of transmission capacity for the delivery of renewable resources (geothermal and solar) from Arizona and the Imperial Valley.
- Increases the reliability and decreases the reliance of remedial action schemes for the broader San Diego/Imperial Valley region for loss of the existing North Gila – Imperial Valley 500 kV line.
- Reduces carbon emissions by decreasing the San Diego area reliance on local gas capacity by as much as 865MW.
- Reduces the congestion on the existing North Gila – Imperial Valley 500 kV line.
- Unlocks stranded capacity west of North Gila under normal and contingency conditions.
Pacific Gas and Electric Company
Submitted 03/14/2022, 04:35 pm
1.
Comment on chapter 1 Introduction:
PG&E appreciates the opportunity to provide comments on the draft study plan for the 2022-23 Transmission Planning Process. Below please find PG&E’s comments and recommendations.
2.
Comment on chapter 2 Reliability Assessment:
Load Forecast Assumptions: PG&E appreciates the effort CAISO and the State agencies, notably the CEC, have made to improve the granular quality of load forecasts in support of the TPP. Given California and Federal policy, as well as market trends, PG&E recommends the CAISO use the CEC’s IEPR high EV load forecast as part of the 2022-2023 TPP base case and for TPP sensitivity analysis. PG&E anticipates that EV demand will continue to accelerate upwards in coming years and supports the CEC’s IEPR high EV forecast as being representative of that trend. The use of the IEPR high EV forecast will help identify transmission investments necessary to support the increase in load from charging EVs.
Reliability Assessment, Generally Sensitivity Studies: The 2024 spring sensitivity case calls for high renewable dispatch at hour ending 8pm in spring. As a majority of the renewable generation in PG&E is solar, such dispatch appears not aligned with the time assumed in the case. Possible alternatives to the base line and sensitivity case selections:
- If the CAISO sees a strong need to have a heavy spring scenario for 2024 spring base line case, stressing COI flow to high N-S level can be an alternative for the sensitivity case. Right now, all the spring cases for PG&E area studies are assuming high S-N flow on COI. While this may be likely in light spring and high solar scenario, such as the 2027 and 2032 spring off peak cases, it is possible, in heavy spring scenario, such as the current 2024 spring case, COI flow can be north to south. In past CAISO special study (COI rating) and recent path rating studies, it was known that high N-S flow on COI in the spring case would be a more severe scenario for transient stability test than summer peak.
- If the CAISO doesn’t have to keep the current 2024 spring baseline case as is, one alternative can be setting the 2024 baseline case to mimic the gross peak load in a spring day. A sensitivity case will be largely reducing or turning off solar in PG&E to mimic a cloudy day in Northern California or other exceptional weather condition and reveal the high demand that is offset from DG to the transmission grid. The overall PG&E load in this sensitivity case could be higher than the net peak at 8pm.
Known Outages: PG&E recommends that the CAISO still include any known outages of generation and transmission facilities longer than six months regardless of single or double outages in the Study Plan’s outage table. That is to meet the TPL-001-4 in 2022 while preparing for the TPL-001-5 reliability standard.
2023 Local Capacity Technical Studies: The CAISO studies identify deficiencies on a local and sub-local area basis. For any LCR area or sub-local area that is deficient, PG&E encourages that in the TPP the CAISO review the limiting contingency in LCR studies, and ensure mitigations are in place for any reliability standard deficiencies identified.
Transmission Service and Market Scheduling Priorities: PG&E requests the CAISO conduct a preliminary assessment of native load needs in the TPP. The CAISO has requested that FERC approve a two-year extension of the interim wheel-through priorities until June 2024. This additional time will be used to create a forward transmission reservation process to allocate capacity between native load and external entities for wheel-throughs, with an implementation schedule expected for early 2024.
In the Draft 2021-2022 Transmission Plan, CAISO recognized that the potential for firm service offerings for wheel-throughs “may have significant impacts on transmission planning.”[1] Prior to implementation of a new framework for wheel-throughs in 2024[2], PG&E is requesting a preliminary assessment within the current 2022-2023 TPP on what the native load transmission needs might be to ensure a reliable California grid on a long-term basis.
[1] CAISO Draft 2021-2022 Transmission Plan. January 31, 2022. Pg. 38 at http://www.caiso.com/InitiativeDocuments/Draft-2021-2022TransmissionPlan.pdf
[2] See Phase 2 implementation timeline of the CAISO’s Transmission service and market scheduling priorities initiative: https://stakeholdercenter.caiso.com/StakeholderInitiatives/Transmission-service-and-market-scheduling-priorities
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
Offshore Wind contributing to Policy-Driven Transmission Projects: The TPP base case scenario includes significant amounts of offshore wind (“OSW”) in the statewide resource portfolio, with planned online dates in the latter part of the planning horizon. PG&E is technology and resource-type agnostic but notes the robust interest among many stakeholders (including state and federal agencies) to encourage development of OSW in California. PG&E acknowledges that the scale of OSW in the base case could result in policy-driven transmission projects as part of the TPP.[1] Given the long development time and complex multi-agency processes, as outlined in several OSW-focused workshops held by the CPUC, CEC, and BOEM in recent months, PG&E encourages CAISO to continue to evaluate and consider transmission solutions that could flexibly integrate OSW resources and other technologies should these resource types be procured. Resource planning activities, such as the CPUC’s IRP, will need clear signals regarding feasibility, timelines, and costs for transmission projects that are needed to make OSW a significant contributor to the State’s resource mix.
[1] Both the 2020-21 TPP special study and the 20-Year Transmission Outlook identified several likely transmission projects to integrate OSW off the California coast.
4.
Comment on chapter 4 Economic Planning Study:
Congestion and Production Benefit Assessment: PG&E appreciates and supports the CAISO’s use of production cost simulation (“PCS”) modeling and asks the Commission to quantify the curtailment of renewable resources due to transmission. This information will be extremely valuable for the future IRP modelling as the IRP models do not reflect local renewable resource curtailments while planning for GHG emission reduction.
Furthermore, PG&E requests that the CAISO conduct an economic study to identify solutions to relieve transmission congestion in the Fresno Avenal area that includes lines such as the Gates-Tulare Lake 70kV line, the Gates Substation, and the Kettleman Hills Tap to Gates 70 kV line. Transmission congestion can increase consumer costs because it prevents low-cost energy from serving customers. The CAISO should study and identify cost effective transmission solutions that would mitigate congestion in the Fresno Avenal area.
5.
Comment on chapter 5 Interregional Transmission Coordination:
Transmission to Integrate Out of State Resources, Generally: The base case portfolio includes significant amounts of out-of-state resources that will require new transmission, according to the CPUC’s preferred system plan. These resources include out-of-state (OOS) wind and geothermal. While the inaugural 20-year Transmission Outlook provides a useful, high level indication of the types of projects that may be necessary to access OOS resources, PG&E encourages CAISO to provide clarity around the feasibility and costs of interconnecting these (and potentially other) OOS resources within the timeframe contemplated by the CPUC’s PSP. For example, significant amounts of these OOS resources are expected to be online and delivering to California by 2028 and 2030. The availability of transmission capacity is an important consideration for the State’s resource planning efforts.
6.
Comment on chapter 6 Other Studies:
Other Studies – Local Capacity Requirement Assessment: PG&E recommends CAISO conduct LCR reduction studies using the new reliability planning standards as part of the 2022-23 CAISO TPP studies.[1] Previously the LCR reduction studies for the 2018-19 CAISO TPP were conducted using the old reliability standards and should be refreshed and reincorporated as part of 2022-23 process. For the CAISO’s LCR reduction studies, PG&E recommends prioritization of Local and Sub Local Areas where there are tight supply conditions. Based on the studies performed in the 2021-2022 transmission planning cycle, several reliability concerns were identified for the PG&E Greater Bay Area. Therefore, PG&E recommends starting the analysis for the Greater Bay Area.
Other Studies – Frequency Response Assessment: PG&E appreciates CAISO’s plan to update the previous frequency response assessment. As noted in the draft study plan, the inverter-based resources (IBR) will continue to increase in proportion of the overall energy mix, and it is extremely important that the CAISO continue to assess the CAISO system’s frequency response ability under a range of scenarios. PG&E recommends that the CAISO augment its assumptions for the dispatch of renewable resources based on its production simulation model results.[2] In addition, PG&E asks that the CAISO report out how many MWs of resources with frequency response capability are assumed to be online in the scenario to provide insight into minimum levels of resources with frequency response capability required to be online to maintain required levels of frequency response capability for the CAISO system. As frequency response is a metric for the overall performance of the entire WECC system, PG&E also suggests the CAISO to review and adjust frequency responsive generation and system inertia in the entire WECC system to match the study scenario more accurately.
Other Studies – Transmission Reliability in LA Basin: PG&E supports having a special study to consider reliability impacts in Southern California. PG&E encourages the CAISO to consider whether there is a minimum generation level and attributes of resources needed to maintain reliability in both the LA Basin and in the closely related San Diego local area, as part of its analysis.
Other Studies – High Electrification Scenario: PG&E supports CAISO considering the impacts of high electrification on reliability needs in the TPP. Connected with a high electrification future, PG&E encourages the CAISO to work with the CEC, CPUC and other stakeholders to consider increased demand from EV adoption as part of its high electrification scenario. PG&E is willing to share the results of its own, internally developed EV load forecast at the bus-level that we believe provides an accurate projection of anticipated EV load consumption in PG&E’s service territory. PG&E anticipates that this additional detail would contribute to a more effective analysis by the CAISO in evaluating local area constraints and reliability needs over the TPP planning horizon.
[1] For e.g., a high renewable dispatch scenario reflects an hour during spring off-peak condition whether the production simulation model shows highest level of renewable generation.
[2] CAISO adopted new transmission planning standards that became effective on September 8, 2018. http://www.caiso.com/Documents/ISOPlanningStandards-September62018.pdf
7.
Please provide any additional comments:
PG&E has no comments on this section.
Vistra Corp.
Submitted 03/16/2022, 04:58 pm
1.
Comment on chapter 1 Introduction:
Vistra Corp. respectfully submits these comments on the CAISO’s 2022-2023 Transmission Planning Process (“TPP”) Draft Study Plan posted on February 18, 2022 and discussed at a stakeholder call on February 28, 2021. We appreciate the CAISO’s continued efforts to focus on advancing the effectiveness of its transmission planning processes in each iteration. Vistra requests the CAISO consider the following requests, detailed further below:
- Economic Study Request for 2022-2023 TPP
- Revise Section 2.7.1, New Generation Projects, to include projects in service in Years 1-5
- Revise cycle life assumption in storage replacement cost estimate
- Provide transparency to difference in planning & operating cost parameters
- Provide transparency into how seasonal line rating values are calculated
2.
Comment on chapter 2 Reliability Assessment:
Revise Section 2.7.1, New Generation Projects, to include projects in service in Years 1-5
Vistra requests the CAISO clarify or where appropriate update the criteria for the first two levels as follows:
- Level 1: Under construction (for Years 1-5 study case with applicable in-service dates)
Vistra requests the CAISO clarify that to meet the criteria for “under construction” is that construction has begun on any work necessary to complete the project, whether this be interconnection facilities, network upgrade facility, or generating facilities. This clarification is essential to provide clarity that when construction begins on necessary work included in the Interconnection Agreement, that the CAISO begins to model the project in its Level 1 category.
- Level 2: Regulatory approval but not yet under construction (i.e., having Power Purchase Agreement approved by the CPUC or other regulatory agencies with applicable in-service dates for Year 5)
Vistra requests the CAISO add two levels to Level 2 – “Regulatory approval but not yet under construction” and “Pending Regulatory Approval”. CAISO could implement this by adding a level in between the current 2 and 3 or by creating levels 2a and 2b. What is important is that if projects have an executed long-term agreement that has been awarded and filed for approval, this means the project has begun to move on the necessary actions needed to achieve the applicable in-service dates in the executed contract pending approval, the same as if it had achieved regulatory approval. In our experience, there is not a meaningful difference between executing an agreement and having it approved, other than there is a risk the project could be rejected, but while that risk exists the development activities cannot wait for the approvals before commencing to ensure the project can achieve commercial operations. Consequently, it is inappropriate for the CAISO to not include projects that have executed agreements since pre-construction activities have likely already commenced.
Vistra requests the CAISO seriously consider these suggestions. We are certain that the 2022-2023 TPP study will not accurately reflect projects for years 1-5 because even with the above request, the Moss Landing Energy Storage 3 project that has an Initial Delivery Date of August 1, 2023 that has been filed for approval by Pacific Gas & Electric (Advice 6477-E[1]) will not be modeled in the Year 1 cases. This means this project that is to achieve commercial operations in 2023 will not be reflected in the local capacity requirements study for 2023 even though it will be in operations either. We put forward this modest request to at least include this project in level 2 for Year 5 case, even though it should be modelled in the cases for Year 1, in an attempt to try to seek a marginal improvement to the CAISO’s modeling approach. This will ensure that at least the CAISO modeling for planning year 10 will be able to reflect the impact of this project that will achieve commercial operations next year.
Finally, Vistra requests clarity on how the CAISO expects Interconnection Customers to communicate to it that the IC has begun construction activities on any necessary work to support the project. Please clarify if the CAISO expects us to communicate this status to the planning group.
[1] Request for Approval of Mid-Term Reliability Procurement Pursuant to D.21-06-035 and D.21-12-015, Advice 6477-E, Table 1, https://www.pge.com/tariffs/assets/pdf/adviceletter/ELEC_6477-E.pdf.
3.
Comment on chapter 3 Policy-Driven RPS Transmission Plan Analysis:
Please see below Vistra's feedback on methodology in response to Question #4, economic planning study. While our methodology comments are included in this response it is critical to recognize that the Production Cost Model (PCM) used in the planning studies are used in economic studies as well. Consequently, Vistra's requests on improvements to PCM used in economic assessments should also apply to the PCM used for policy-driven assessments.
4.
Comment on chapter 4 Economic Planning Study:
Economic Study Request for 2022-2023 TPP
In the 2021-2022 TPP, the CAISO is recommending an economic project on the Moss Landing – Las Aguilas 230kV line. In 2021-2022 TPP, the CAISO observed over $13.8 million in annual congestion cost on Moss Landing – Las Aguilas 230 kV line and identified a net benefit of installing a 10 Ohms series reactor on the congested line as a congestion mitigation alternative. The CAISO economic study shows the recommended economic project saves $5.6 million for CAISO ratepayers annually. We appreciate CAISO’s analysis and agree that there is a need for projects to solve this congestion.
Vistra is continuing to develop battery energy storage at the Moss Landing site in the time frame being studied in the 2022-2023 TPP. Vistra has a long-term RA agreement for the Moss Landing Energy Storage 3 project for 300 MW / 1,200 MWh with an Initial Delivery Date of August 1, 2023 pending approval at the California Public Utility Commission. With the additional battery energy storage capacity at Moss Landing, we believe that there will be greater congestion levels identified in the 2022-2023 TPP than identified last iteration where this capacity was not modelled.
Vistra requests the CAISO review the scope of the recommended project, the 10 Ohms series reactor, to see whether the scope may not be sufficient to resolve the expected increased line congestion with the additional 300 MW modelled. Specifically, Vistra requests the CAISO conduct an economic study of a transmission project to reconductor the Moss Landing – Las Aguilas 230 kV line to increase the line rating to 800 MVA.
Revise cycle life assumption in storage replacement cost estimate
Vistra appreciates the CAISO updating the battery cost model and depth of discharge approach to estimating the average cost of battery dispatch discussed in the last TPP cycle. In our comments on the Draft Study Plan submitted on March 11, 2021, Vistra requested the CAISO revisit its approach for estimating these values, including the recommendation to update the input values using the updated PNNL report, 2020 Grid Energy Storage Technology Cost and Performance Assessment, published in December 2020 that expanded the forecasts to 2030. In last iteration, the CAISO updated its battery operation cost estimate by using Figure 2 in the 2020 PNNL study for the 100 MW / 4 hr battery storage block value of $99,000/MWh and maintained the following assumptions:
- Cycle life: 2,100
- Calendar life: 10
- Depth of discharge: 80%
- Cycles per day: 1
The resulting battery energy storage replacement cost estimate used in the 2021-2022 TPP based on this methodology is ~$29/MWh:
While updating the replacement cost is an improvement, the cost estimate is still inconsistent with expected operations of battery energy storage achieving commercial operations in recent years and in the future. While the nascent technology limited cycles per day, largely through annual use limitations, this is no longer true for the large-scale battery energy storage resources achieving commercial operation in the last few years; nor, is the assumption that resources have a useful life of 10 years. For resources with longer calendar lives as can be seen in their long-term RA and power purchase agreements, this estimate is inflating the operating costs of those resources that can plan more efficiently for augmentation needs across a longer life cycle.
However, as a starting place to improve this value, Vistra requests the CAISO at a minimum assume that battery energy storage would cycle once a day across a 10-year useful life, which is 3,650. We illustrate the change in flat average replacement costs using an improved cycle life assumption.
As Vistra’s Moss Landing Phase 1 Facility has a 20-year useful life approved under a long-term agreement[2], we are uniquely situated to understand that the 10-year useful life assumption is an overly conservative assumption. With this experience, we are confident this is a modest update.
The updated cost estimate at ~$17/MWh is more in line with industry expectations than the existing approach. We respectfully urge the CAISO to update the replacement cost estimate accordingly to better represent battery economics in this TPP cycle. We are optimistic the CAISO will be open to further updating this approach by also including this updated cycle life assumption in the upcoming 2022-2023 TPP cycle. This will further improve the accuracy of the CAISO’s modeling of storage operations.
Provide transparency to difference in planning & operating cost parameters
Vistra understands that CAISO uses the operating parameters and Variable Operations and Maintenance adders from the PCM Anchor Data Set. Vistra requests the CAISO seek to reconcile the PCM Anchor Data Set with Master File registered values where possible. In the instance there is a discrepancy between the PCM Anchor Data Set and resource’s registered operating characteristics, Vistra requests the CAISO provide transparency into how either value was selected.
Provide transparency into how seasonal line rating values are calculated
Vistra has observed transmission line ratings in the Transmission Planning Process models where the line ratings are established at higher transmission line ratings than we frequently see in operations. In some cases, the dynamic line ratings observed for normal rating and emergency rating for operations are meaningfully short of the high-end values that we believe the CAISO is using to model the system. Vistra appreciates the CAISO clarifying that it is modelling seasonal ratings as registered in the Transmission Register at the stakeholder call. We further request clarification on how the CAISO arrives to the two seasonal values for transmission lines that have dynamic ratings that vary during the seasons. We note that FERC found in Order No. 881 that “AARs [ambient adjusted ratings] used in near-term operations will deviate from those transmission line ratings used in various planning functions.”[3] For instance, does the CAISO use the dynamic ratings during a season that is an average, minimum, maximum, or some other value to establish the single seasonal value for planning modeling purposes?
[2] CPUC Resolution E-5049, January 16, 2020, Page 3, Table 1, https://docs.cpuc.ca.gov/PublishedDocs/Published/G000/M325/K120/325120337.PDF.
[3] Managing Transmission Line Ratings, 177 FERC ¶ 61,179 at P 131 (2021) (Order No. 881).
5.
Comment on chapter 5 Interregional Transmission Coordination:
Vistra is looking forward to CAISO exploring the interregional projects submitted by the end of this month.
6.
Comment on chapter 6 Other Studies:
Vistra requests the CAISO include the planned generation projects as requested in response to Question #2 in the local capacity requirement studies as well. We further request the LCR adopt any of the PCM improvements that we are requesting that would apply to the LCR study that we request in response to Question #4.
7.
Please provide any additional comments:
None at this time.